关于BS 1363-2的几个问题请教
发表于 2012-2-4 14:08:10 | 只看该作者 回帖奖励 |倒序浏览 |阅读模式
11.5 Line and neutral terminals in fiexed socket-outlets shall permit the connection, without special preparation, of one, two or three 2.5mm2 solid or stranded or one or two 4 mm2 stranded conductors.
固定式插座的相和中性端子应能连接1,2,或3根2.5mm2实心或绞合线,或1或2根4mm2绞合导线。
如果进行试验时,对相和中性端子对标准列举的5种,都需试验吗?接上3根2.5mm2导线试验,觉得好象不太符合实际情况。
13.4…………The means for producing the contact pressure shall be associated with each socket contact independently…………
这句话是如何理解的?
13.4.1a) ………the voltage drop is mesured between the terminal connecting strap at a point immediately adjacent to the socket contact and the correspondinggg plug pin………
还是没看明白在插套和插销的哪两个部位之间测量电压降。
13.5.1 ………… the socket-outlet is mounted with the engagement face in the vertical plane and with the major axis of the line and neutral pins horizontal…………
哪里算插销或插孔的主轴?如果算插孔或插销轴线的话,可以多个方位啊,比方说接地孔在上或在侧面。
13.16…… Flush or semi-flush mounted socket-outlet plate shall have provision for tow M3.5 fixing screws at centres of 60.3mm on horizontal or vertical centrelines for boxed intended to accommodate 1-gang socket-outlets……
这句话什么意思??
先行谢过。。