如何理解 SAA 插座 高压测试要求
发表于 2012-2-3 17:12:00 | 只看该作者 回帖奖励 |倒序浏览 |阅读模式
有没有哪位清楚SAA 插座 高压测试要求,对地线脚的高压测试是多少伏?
The socket-outlet shall withstand, without failure, an a.c. voltage of the value indicated in Table 3.3 applied between the parts set out in Items (a) and (c) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall further withstand, without failure, a voltage of 3500 V a.c. applied between the parts set out in Items (b) and (d) of Clause 3.14.2 for 1 min in each case. The socket-outlet shall be fitted with an appropriate plug during the test.
TABLE 3.3 TEST VOLTAGES FOR HIGH VOLTAGE TEST
Working voltage (r.m.s.) between parts (See Note) Testing voltage
≤ 32 V 500 V
> 32 V ≤250 V 1 000 V
>250 V ≤650 V 1 000 V + (2 ×working voltage) with a maximum of 2000 V
NOTE: For example, a socket-outlet for connection to a system operating at 415 V between phases and 240 V to earth, would require a test of 1000 + (2 × 415) V between live terminals but a test of only 1000 V between live parts and earth.
3.14.2
d,Between live terminals of the socket-outlet and the earthing terminal (if any), with the live terminals of the plug being connected together.
发表于 2012-2-3 17:12:05 | 只看该作者
1000V啊!
 楼主| 发表于 2012-2-3 17:12:11 | 只看该作者
d,Between live terminals of the socket-outlet and the earthing terminal (if any), with the live terminals of the plug being connected together. --如何理解?