求助壁炉的验货要点和要求!
发表于 2011-3-4 09:52:20 | 只看该作者 回帖奖励 |倒序浏览 |阅读模式
有哪位大哥大姐有壁炉的验货要点和要求!麻烦发过来我参考参考!谢谢了!
发表于 2011-3-4 10:28:51 | 只看该作者
路过。。。。。。。。。
发表于 2011-3-4 10:51:36 | 只看该作者
Insert:
1)风机(风机没有功能,或者转速低)
2)功率(有时只有一组发热丝工作,所以功率只有50%)
3)灯泡不亮,或者只亮一个,或者用错规格(看功率)
4)把出风口堵住,看温控是否自行断开
5)很多工厂在发热丝上涂有防锈油,导致在开机的一瞬间有大量浓烟冒出
6)发热丝附近不允许有线,以及可燃物,下面的塑料支架不能点燃
7)噪音不能过大
8)玻璃的钢化测试
Mantel:
1)无法组装
2)发霉,长毛
3)KD 孔位打错
2. FUNCTION TEST        Qty        Pass        Fail        N/A
A) Dielectric Withstand Test        20        X
- Withstands without breakdown a potential of 1000vac / 5mA (1000vac + 2 times the rated voltage for
units rated more than 250V) applied for 1 minute between live parts and any noncurrect-carrying
B) Strain Relief Test: (for Power Supply Cord)        3        X
- The strain relief device withstands a 35lbs pull force applied for 1 minute in any direct without
transmitting the pull to terminals, splices or internal wiring.
(RESULTS - There is to be no displacement of nor strain transferred to that portion of power supply
cord internal to the test sample.)
C) Stability Test        3        X
- Moveable heater returns to its intended at-rest postion on level surface when tipped in any
direction at an angle 10 Degree to the horizontal
D) Glass Panel Impact Test        3        X
- A glass panel or similar brittle material employed in a heater withstands, without cracking
or breakage, an impact producted by swinging a 2 inch diameter steel sphere weighing        toughened glass:377mmX357mmX5mm
1.18lbs from a height of 16.15inches.        plastic panel:371mmX279mmX2.5mm
(The panel, while in fully heated conditsion, does not crack or break when a wet cloth is wiped
across the surface or when sprayed with a fine mist of cold tal water.)
5) Switch Durability: (Switches must withstand 100 Cycles of use w/ no failure)        3        X
6) Wattage Testing+5%-10%)        10        X
        Volt /Hz        Amp        Wattage        Condition                Volt / Hz                Amp        Wattage                Condiftion
Sample 1        120V/50Hz        12.05A        1438W        All Switches On                135V / 50Hz                13.99A        1884W                Overvoltage Test
Sample 2        "        12.13        1472        "                "                13.92        1868                "
Sample 3        "        12.05        1436        "                "                14.01        1898                "
Sample 4        "        12.09        1522        "                "                14.05        1910                "
Sample 5        "        12.04        1535        "                "                14.09        1907                "
Sample 6        "        12.28        1466        "                "                13.99        1884                "
Sample 7        "        12.43        1544        "                "                14.09        1913                "
Sample 8        "        12.59        1519        "                "                14.16        1930                "
Sample 9        "        12.66        1534        "                "                14.11        1911                "
Sample 10        "        12.72        1539        "                "                14.27        1923                "
7) Light Bulb Life Test (For B10 - 40W)        3        X
- Input Power (162Vac / 50Hz)                                  REMARK:
8) Overrall Appearance        20                X
- No major defect, no loosening of parts/ component, well painted, no burrs, cracks or dents
9) Construction        3        X
- All component shall be UL/CUL and CSA recognized
10) Workmenship        20        X
- Good finish, no sharp edge, no sharp point, properly fitted
- All feet can be assembled well and level
- Door is properly assembled, can be opened and closed normally
- Glass window is properly fitted
- Clip holding glass window is assembly properly