电线要求:
芯线:
2.2 INSULATION
2.2.1 Material
Insulation shall comply with the requirements of one of the following materials, in
accordance with AS/NZS 3808:
Material groups Designation
Cross-linked elastomeric R-EP-90. R-CSP-90,R-CPE-90, R-S-150,R-S-200
外被:
2.6 SHEATH
2.6.1 Material
To operate the conductor at the maximum temperature appropriate for the insulation, the
temperature rating of the outer and/or inner sheath may be less than that of the insulation by
not more than 5°C. For cables with R-S-150 and R-S-200 insulation the maximum
conductor temperature shall be limited to be not higher than 5°C above the maximum
permitted for the selected sheath material.
Sheath shall comply with the requirements of one of the following materials, in accordance
with AS/NZS 3808:
Material groups Designation
Cross-linked elastomeric GP-85-PCP, HD-85-PCP,GP-90-CSP, HD-90-CSP,GP-90-CPE, HD-90-CPE,GP-150-S
去看AS 3191-2008 的Table 2.5的第2,第3条
2 All tests on insulation taken from ormeasured on the completed cord (seeNote 1)
As specified in AS/NZS 3808 for the relevant insulation designation
3 All tests on sheath taken from ormeasured on the completed cord
As specified in AS/NZS 3808 for the relevant sheath designation
NOTES:
1 For the 250/250 V PVC insulated, unsheathed, parallel-webbed 2-core flat flexible cords with tinsel conductors, the insulation resistance constant (ki) shall be not less than 10 GΩ.m at 20°C and 0.005 GΩ.m at 75°C.
老化条件:
去看AS 3808-2004的Table1和Table2
90类芯线135±3℃ 168h
105类芯线150±3℃ 168h
..........
具体自己看了。 |
|