Electrical test-UL1598(2)
工厂生产测试
15.1 Dielectric voltage-withstand
绝缘材料耐压性
15.1.1
A dielectric voltage-withstand test shall be performed on 100 percent of production of luminaires that contain conductors that are:
灯具上的导电线具有下列特点的, 在生产过程中要作100%的绝缘材料耐用压测试.
a)not visible after assembly; or
组装以后看不见,或
b) enclosed for a distance more than 38 mm (1.50 in) within:
位于杆部、臂部或管状部分壳体内,或是未列上清单的或是没有经认证过的导线管内,深度达38 mm (1.50 in)。
1)a stem, arm, or tubing; or
2) conduit that is not Listed or Certified.
15.1.2
A fluorescent luminaire with the construction described in Clause 15.1.1 and provided with a removable cover for access to conductors shall not be required to be subjected to the factory dielectric voltage-withstand test.
结构如第15.1.1条所描述,还有一个供导线引进引出的日光灯具的活动盖子的日光灯灯具不要求一定要作绝缘材料耐压测试。
15.1.3
The dielectric voltage-withstand test apparatus shall be in accordance with Clause 16.20.
绝缘材料耐压性能测试设备应符合第16.20条的要求.
15.1.4
Luminaires shall be fully assembled, with control and protective components in conducting position, switches in the ON position, and fuses in place. Isolated non-current-carrying metal parts or decorative parts not likely to become energized shall not be required to be in place.
灯具要完全组装好,控制器和保护性组件组于通电状态,开关处于“ON”的位置,保险丝也在位。
已绝缘的非载流金属部件或不可能通电的装饰性部件不要求装配到位。
15.1.5
Solid state components not relied upon to reduce the risk of electric shock and that may be damaged by the applied dielectric potential may be disconnected for the test. The circuitry may be rearranged for the purpose of the test to reduce the likelihood of solid state component damage while retaining the representative dielectric stress on the circuit.
不可能用来减少电击风险或有可能被所加的绝缘测试电压损伤的固态组件可以为测试而断开连接。电路上某段出现尖峰电压时,为了测试,可以将电路重新安排,以减少固态组件受损的可能性。
15.1.6
The test shall be conducted by applying a voltage of 1200 V ac, for a duration of one second, without dielectric breakdown, between:
测试用电压为1200V AC,持续时间为1秒,没有绝缘击穿,
测试要在下列两处进行,
a)Primary wiring and accessible non-current-carrying metal parts that may become energized; and
初级电路和有可能会带上电的可接触非载流金属部件之间,还有
b) Primary wiring and accessible uninsulated live parts in the secondary circuit of an isolating transformer rated for a maximum open circuit voltage of 30 volts rms or 42.4 volts peak.
初级电路和一个电大的额定开路电压为30 volts rms或是峰值电压为42.4 volts的已绝缘的变压器上的次级电路上的未绝缘可接触的带电部件。
15.2 Grounding continuity
接地的连贯性
15.2.1 General
概述
15.2.1.1
A grounding continuity test shall be performed on luminaires with:
具有下列部件的灯具要求作接地连贯性的测试:
|
|