5.1 Spark test after insulating  
 
 
The voltage source of a dc or ac spark tester shall maintain the following test voltage under all nor 
 
mal conditions of leakage current:  
 
a) An essentially sinusoidal rms potential of 1750 V for an ac test;  
 
b) 2500 V for a dc test. The current output of which the dc power supply is capable shall not exceed 
 
 5 mA. Any ripple shall not exceed 1 per cent. After a fault, the dc test voltage shall recover to the full  
 
test voltage in 5 ms or less, unless 610 mm (2 ft) or less of the product travels through the electrode 
e in the time that it takes for the full voltage recovery;  
 
c) For conductor gauge sizes 22 – 30 AWG which are to be used in cables without coaxial membe 
 
rs but with foam or foam skin insulation and protected by bonded metal shields, the following spar 
 
k test voltage may be used:  
 Conductor size Test Voltage  
 22, 23 AWG 1500 V dc or 1050 V ac  
 24, 25 AWG 1200 V dc or 850 V ac  
 26–30AWG 1000Vdcor750Vac  
 
d) For cables without bonded metal shields, and with foam insulation that is not more than 0.20 m 
 
m (0.008 in) in average thickness and does not have a skin, the spark test voltage may be reduced 
 
 to 1250 V ac or 1750 V dc, provided that the dielectric strength test voltage required by Clause  
 
5.3.5 is met.  
  
这段内容看得有点糊涂,前辈们可否指导一下? 
问题1. 首先我不理解d)中所涉及的skin在实物中是什么? 
问题2. c)中foam 和foam skin 有何区别? 
我想先把这个问题搞清楚了 |   
 
 
 
 |