The test voltage for the luminaire shall be as follows.
– Filament lamp luminaires other than ELV: that voltage which produces 1,05 times the
rated wattage of the test lamp (see Annex B) except that heat test source (HTS) lamps
are always operated at the voltage marked on the lamp.
– Tubular fluorescent and other discharge lamp luminaires and ELV luminaires with
tungsten filament lamps: 1,06 times the rated voltage or the maximum of the rated
voltage range.
– For motors contained in luminaires: 1,06 times the rated voltage (or the maximum of the
rated voltage range of the luminaire).
Exception
For determination of the average tem作者: 月色浪漫 时间: 2012-1-21 01:16
哪一种都不是,我们一般用1.06倍额定电压